In Slab Conduit - Failed Inspection
« on: January 20, 2016, 11:51:58 AM »
We failed an inspection this morning. At this location there is one PVC conduit, about 50' that stubs up into a cabinet with 4 Cat 5e cables.  The inspector is requiring us to install moisture-proof cable, instead of CMR.  While I know he is technically right, we always use CMR.  Sometimes it's like trying to hit a moving target with this one AHJ.

Offline EV607797

  • Moderator
  • Location: Northern Virginia (Metro DC Area)
  • Posts: 717
Re: In Slab Conduit - Failed Inspection
« Reply #1 on: January 20, 2016, 01:08:35 PM »
Did the inspector cite an NEC article number?  No, because there isn't one.  Besides, filled cable of any type is not rated for indoor use, even if it's in a conduit under a slab since the cable eventually emerges from the conduit.
Ed Vaughn

(540) 623-7100 (V)  (540) 693-5800 (F)
EMVaughn3@Outlook.com

Offline Marc Haycook

  • Administrator
  • Location: Jefferson City, MO
  • Posts: 2626
Re: In Slab Conduit - Failed Inspection
« Reply #2 on: January 21, 2016, 03:29:46 PM »
Besides, filled cable of any type is not rated for indoor use, even if it's in a conduit under a slab since the cable eventually emerges from the conduit.

That's correct because it emits a toxic gas if it is burned.  :035:
Marc Haycook
CCNA
Sport-Touring

Offline NFCphoneman

  • Moderator
  • Location: Jacksonville & Gainesville, FL
  • Posts: 649
    • Jacksonville Telephone Systems
Re: In Slab Conduit - Failed Inspection
« Reply #3 on: January 21, 2016, 04:01:48 PM »
I wasn't there, and my tech didn't ask for a reference.  NEC 2014, Article 100 does define a wet location as: “Installations underground or in concrete slabs or masonry in direct contact with the earth..." So, I can't argue that it is a wet location.

I also know that you can't go more than 50' outside of a conduit with the OSP cable. Fortunately, that shouldn't be a problem at this site. Otherwise, we have to put in a transition point.

Am I the only one lucky enough to run into this?

Offline MacGyver

  • Administrator
  • Location: Dallas, Texas
  • Posts: 3883
Re: In Slab Conduit - Failed Inspection
« Reply #4 on: January 21, 2016, 04:31:51 PM »
NEC 2014, Article 100 does define a wet location as: “Installations underground or in concrete slabs or masonry in direct contact with the earth..."

But you're not in direct contact with the earth or the slab.  Aren't you in a PVC conduit?  I would understand if you were running in EMT.

-I'm only here because my flux capacitor is broken.

Offline NFCphoneman

  • Moderator
  • Location: Jacksonville & Gainesville, FL
  • Posts: 649
    • Jacksonville Telephone Systems
Re: In Slab Conduit - Failed Inspection
« Reply #5 on: January 21, 2016, 05:40:17 PM »
It's in PVC conduit. My understanding is that if the conduit is in a "wet" location, then the conductors have to be as well, and least in the electrical world.

For more confusion, see:  https://forums.mikeholt.com/showthread.php?t=146617

https://forums.mikeholt.com/showthread.php?t=103535

http://ce.superioressex.com/uploadedFiles/docs/pdf/technical-guidelines/TG58-Copper-TP-Below-Grade-Conduit.pdf

Online hbiss

  • Administrator
  • Location: Westchester County, NY
  • Posts: 2863
Re: In Slab Conduit - Failed Inspection
« Reply #6 on: January 22, 2016, 09:12:26 AM »
Don't confuse conductors with LV or communications cable. Communications cable is covered by Art 800. Most of Art.725 and 800 on stands alone from the rest of the NEC. Nothing in the previous chapters applies to 725 and 800 on unless there is something that specifically says to refer back to an article in the front of the book. So, yes, PVC underground or in a slab on grade is a wet location. If you were running power through it then there are rules you must observe. But you are not, this is communications and the article that applies says nothing about wet locations. This is a design issue and if you feel CMR will be OK that's your call.

Understand that the NEC is about protecting lives and property. If power wiring is improperly run in a wet location it could deteriorate and cause damage. If your data wiring deteriorates nobody is going to get hurt.   

-Hal
I gotta get out of this business...


COMSYSTEC- Phone Systems | paging systems | background music systems | foreground music systems | retail music | restaurant music

Offline NFCphoneman

  • Moderator
  • Location: Jacksonville & Gainesville, FL
  • Posts: 649
    • Jacksonville Telephone Systems
Re: In Slab Conduit - Failed Inspection
« Reply #7 on: January 22, 2016, 12:58:56 PM »
Thanks Hal.

Offline tonyburkhart

  • Moderator
  • Location: Reynoldsburg Ohio USA
  • Posts: 993
    • www.burkhartinc.com
Re: In Slab Conduit - Failed Inspection
« Reply #8 on: January 25, 2016, 10:18:04 PM »
This happened to us, in a different sense and we retroactively installed the filled cable. We had a manufacturing facility with an operators/control area about 80' from the closest IDF. We installed CMR in 1999 during the new build, and in 2012, when I was starting my own company, the client called me on my cell and said they had constant problems over the last few months. They had called the company I used to work for, and unfortunately had 3 billable trips with no solution. I recalled that run, specifically, and told them to have their maintenance guy get the cable at Graybar (they had their own account) and pull it through. Then told them to call me back when it was done, and I'd terminate and test. Done, and done, and it worked perfectly.

I did it for $120 + 2 Cat5e ends, and 2 patch cords. My previous employer has billed them for $600+ and NOT, I repeat NOT fixed it. Completely embarrassing, and I told them to call and see if they could get a credit... guess how that went :)

Any way - never knew about the toxic fumes, related to an in PVC vs CMR - makes sense. I always learn something new on this board. Love it
Thanks,
Tony Burkhart
Burkhart Inc.
www.burkhartinc.com

Online hbiss

  • Administrator
  • Location: Westchester County, NY
  • Posts: 2863
Re: In Slab Conduit - Failed Inspection
« Reply #9 on: January 26, 2016, 12:39:10 PM »
Quote
Any way - never knew about the toxic fumes, related to an in PVC vs CMR - makes sense.

What Ed and Marc are talking about is that the jel or grease in filled cable is flammable. This is why you will never see a filled cable with a listing and that means you are limited to how far you can go into a building with it unless you run it in conduit.

As for PVC vs CMR, you are thinking apples to oranges. As long as we are talking about a CM listed cables (communications multipurpose)- CM printed on the jacket means it is the least fire retardant and least capable of not producing toxic fumes. It's use is somewhat restricted.

Next up is CMR. The "R" means riser and that allows it to be used in vertical runs between floors because its jacket compound limits the transmission of flame in an upward direction. Generally you would use CMR for most wiring as it's only pennies more than CM and you don't have to worry about where you run it.

At the top of the list is CMP. The "P" stands for plenum. The jacket of this cable emits limited toxic fumes when ignited and must be used in all environmental air handling spaces although it can be used in place of CM and CMR if you wanted to spend the money.

Note that all these cables are constructed with some version of a PVC jacket, only the compounding varies. (It used to be that CMP was manufactured with a teflon jacket but I haven' seen that in a million years.)

-Hal
I gotta get out of this business...


COMSYSTEC- Phone Systems | paging systems | background music systems | foreground music systems | retail music | restaurant music

Offline NFCphoneman

  • Moderator
  • Location: Jacksonville & Gainesville, FL
  • Posts: 649
    • Jacksonville Telephone Systems
Re: In Slab Conduit - Failed Inspection
« Reply #10 on: February 02, 2016, 10:31:38 AM »
Yesterday I took a class at the BICSI Winter Conference entitled "Applying the NEC to Telecom Design".  As luck would have it, one of the things covered was this exact topic.  It would appear that the inspector was correct, this is a "wet" location.

Since this was network cabling, it would be covered under Article 725. In the 2014 NEC, paragraph L was added which states:   Corrosive, Damp, Wet Locations. Class 2 and Class 3 cables installed in corrosive, damp, or wet locations shall comply with the applicable requirements in 110.11, 300.5(B), 300.6, 300.9 and 310(G).

300.5(B) says "cables installed in these enclosures (conduit in wet locations) shall comply with 310.10(C).

310.10 (C) Wet Locations. Insulated conductors and cables used in wet locations shall comply with one of the following:
(1) Be moisture-impervious metal-sheathed
(2) Be types MTW, RHW, RHW-2, TW, THW, THW-2,
THHW, THWN, THWN-2, XHHW, XHHW-2, ZW
(3) Be of a type listed for use in wet locations

To my knowledge, the code does not list any indoor cable for underground use. I assume that means we're supposed to find a manufacturer who has a cable listed for wet locations that is type CMP, CMR or CM?  Anybody know of such a Cat 5e cable?

IMO, the code sections that apply to our industry need to be re-written. Or, I need a law degree to understand it...

Online hbiss

  • Administrator
  • Location: Westchester County, NY
  • Posts: 2863
Re: In Slab Conduit - Failed Inspection
« Reply #11 on: February 02, 2016, 12:00:18 PM »
Question is are you on the 2014 code cycle? Very few places are, we in NY are still on the 2008. I have to admit that I haven't seen the 2014 probably because we'll never have it here in my lifetime. Regardless, there was always the question of where data cabling belongs. You mention Art 725, I maintain that it belongs in 800 because it's no different than phone wiring. Has the 2014 code clarified that?

-Hal
I gotta get out of this business...


COMSYSTEC- Phone Systems | paging systems | background music systems | foreground music systems | retail music | restaurant music

Offline NFCphoneman

  • Moderator
  • Location: Jacksonville & Gainesville, FL
  • Posts: 649
    • Jacksonville Telephone Systems
Re: In Slab Conduit - Failed Inspection
« Reply #12 on: February 02, 2016, 12:59:40 PM »
Guess it depends on who you ask.  :015:

The NEC Handbook states: The scope of Article 725 includes such systems as burglar alarm circuits (see Exhibit 725.1), access control circuits, sound circuits, nurse call circuits, intercom circuits, some computer network systems, some control circuits for lighting dimmer systems, and some low-voltage control circuits that originate from listed appliances or from listed computer equipment.

Another part of the handbook says: If the wiring leaves the group of equipment to connect to other devices in the same room or elsewhere in the building, the wiring is considered “wiring within buildings” and is subject to the requirements of Article 725.

But, if it was covered under 800, then my comments above do not apply. 800 did not have a reference added back to 3xx.

I don't really know if this particular AHJ is using 2008 or 2014. Quite frankly, we just replaced the cable with some Cat 5e direct buriable and got finaled.

Online hbiss

  • Administrator
  • Location: Westchester County, NY
  • Posts: 2863
Re: In Slab Conduit - Failed Inspection
« Reply #13 on: February 02, 2016, 03:16:09 PM »
Don't forget the 2011 code. New code comes out every three years. They are already talking about the 2017.

Opinion is that the NEC has lost a lot of credibility because they have apparently been "bought" by manufacturers in order to sell their products. Prime example is the AFCI (arc fault circuit breaker) fiasco where they have never been independently proven to do anything except false trip and cost $$$ money. Another is the tamper proof receptacle when it was shown that some kid stuck his elbow in one of the slots of a normal receptacle.

-Hal
I gotta get out of this business...


COMSYSTEC- Phone Systems | paging systems | background music systems | foreground music systems | retail music | restaurant music

Offline ttech

  • Moderator
  • Location: Paoli, PA
  • Posts: 238
Re: In Slab Conduit - Failed Inspection
« Reply #14 on: February 02, 2016, 05:38:36 PM »

Offline NFCphoneman

  • Moderator
  • Location: Jacksonville & Gainesville, FL
  • Posts: 649
    • Jacksonville Telephone Systems
Re: In Slab Conduit - Failed Inspection
« Reply #15 on: February 02, 2016, 07:35:57 PM »
So... is an riser/outdoor rated CMX type cable comply?

http://ce.superioressex.com/uploadedFiles/Docs/PDF/Catalogs/Communications/CAT3-Station-Wire.pdf


That's Cat 3. The link also states: Do not use in conduit or direct burial which can flood. These cables are not designed for extended exposure to water.

Offline ttech

  • Moderator
  • Location: Paoli, PA
  • Posts: 238
Re: In Slab Conduit - Failed Inspection
« Reply #16 on: February 03, 2016, 12:09:03 AM »
Yeah. I missed the red writing. 

Offline ttech

  • Moderator
  • Location: Paoli, PA
  • Posts: 238
Re: In Slab Conduit - Failed Inspection
« Reply #17 on: February 03, 2016, 12:10:39 AM »
They do make it in Cat5e as well.

Online hbiss

  • Administrator
  • Location: Westchester County, NY
  • Posts: 2863
Re: In Slab Conduit - Failed Inspection
« Reply #18 on: February 03, 2016, 09:51:19 AM »
The "X" designation means it's for exterior use basically because it's UV resistant and may have a heavier jacket that's remains flexible under low temperatures. If you look at the tables in say Art 800 you will see that it's use is limited within structures. It's not waterproof.

An interesting thought just came to me about this. A conduit embedded in a slab under a building is not considered in the building. So it wouldn't be improper to use flooded direct burial cable as long as it transitioned to a listed cable within 50 feet or you continued the run in conduit. Problem is if this was a big bundle I wouldn't want all that flooded cable terminating on a patch panel in one place.

-Hal
I gotta get out of this business...


COMSYSTEC- Phone Systems | paging systems | background music systems | foreground music systems | retail music | restaurant music

Offline NFCphoneman

  • Moderator
  • Location: Jacksonville & Gainesville, FL
  • Posts: 649
    • Jacksonville Telephone Systems
Re: In Slab Conduit - Failed Inspection
« Reply #19 on: February 03, 2016, 12:19:32 PM »
An interesting thought just came to me about this. A conduit embedded in a slab under a building is not considered in the building. So it wouldn't be improper to use flooded direct burial cable as long as it transitioned to a listed cable within 50 feet or you continued the run in conduit. Problem is if this was a big bundle I wouldn't want all that flooded cable terminating on a patch panel in one place.

-Hal

A couple of thoughts... It could be continued in conduit, but it would have to be IMC or RMC, couldn't be in PVC or EMT.

So, if you use flooded cable, and your conduit penetrates greater than 50 away from the telecommunications room, then you have to have a transition point.  But, wouldn't that TP have to be an enclosure of some sorts? (Not many of those made for this purpose.)  Then you also have the jack side to deal with. You would have to terminate the flooded cable directly to the jacks, or add a second transition point.  Well, you're not supposed to install more than one TP per run.

Keep in mind that this also depends on which article is covering this cable, 725 or 800. Correct me if I'm wrong, but 725 doesn't mention anything about an allowance for unlisted cable.  Does that mean you're not supposed to use it?

If the installation is falling under 800, then you could use the unlisted flooded cable as long as your don't exceed the 50' rule.  But, if it fell under 800 then you wouldn't have to used the flooded cable at all because 800 doesn't reference back to 300.5(B).

Online hbiss

  • Administrator
  • Location: Westchester County, NY
  • Posts: 2863
Re: In Slab Conduit - Failed Inspection
« Reply #20 on: February 03, 2016, 10:27:19 PM »
This is where the Code falls short. It isn't a problem with CL2 or CL3 wiring. The splice (transition) doesn't even have to be in a box, only accessible. If you can do something like this with data it isn't going to be easy.

Quote
Keep in mind that this also depends on which article is covering this cable, 725 or 800. Correct me if I'm wrong, but 725 doesn't mention anything about an allowance for unlisted cable.  Does that mean you're not supposed to use it?

It's in 800 because it and subsequent articles deal with cables entering from the outside. That doesn't happen with 725 except in certain instances, irrigation and LV landscape lighting come to mind. It's common practice to run the direct burial landscape lighting wire into a structure to connect with the transformer. That cable had no listing so that was a violation. Only recently has a listed cable been available, so in at least this case there is some evidence that demand generates a product.

-Hal
I gotta get out of this business...


COMSYSTEC- Phone Systems | paging systems | background music systems | foreground music systems | retail music | restaurant music

Offline EV607797

  • Moderator
  • Location: Northern Virginia (Metro DC Area)
  • Posts: 717
Re: In Slab Conduit - Failed Inspection
« Reply #21 on: February 06, 2016, 12:49:57 AM »
Welcome to the world of confusion in the NEC.  We all need to buckle up for the ride.

It's all about what manufacturers have to sell for the year that make the rules there anymore,  It's a well-known fact that the board of the NEC is comprised largely of representatives of manufacturers.

GFI protection was the new highly-profitable requirement in the early 70s.  AIC interrupting ratings for breakers and fuses became the 'mandate du jour' in the 80s.  Four-wire dryer and range circuits in the early 90s.  In-use covers for outdoor receptacles in the late 90s.  AFCI protection, tamper-resistant receptacles, etc. since then.  The NEC  has become the National Enquirer of documents these days.  I swear that Arlington Industries owns the NEC.

Still, we have to follow it.

The problem is that the NEC doesn't address the specific situation that Larry's company encountered.  It shouldn't have.  This is not a matter of life safety and property protection, which is the intent of the NEC.  OK, maybe they could stretch the life safety part with the filled cable risks, but that really is a stretch.  Using filled cable that is terminated on anything but a BET rated for such is simply wrong.  Filled cable on a jack module?  Come on...

The truth is, petroleum-based filling compounds aren't the biggest risk.  It's more about the polyethylene jacket that creates the potential fire hazard.  PE also emits poisonous gas when burned.  The goo in filled cable is not always flammable, but it is still incredibly messy and should never be left exposed, since it oozes forever.

On the same token, it is clearly understood that the NEC is not intended to be a design standard.  This whole conversation brings to light the double standard that exists between the code making panel (manufacturers) and the enforcers (AHJ personnel).

Maybe some cable manufacturer needs to come along with an appropriate cable to fit these applications, patent it and then secure a seat on the NEC board so that it can be mandated.
Ed Vaughn

(540) 623-7100 (V)  (540) 693-5800 (F)
EMVaughn3@Outlook.com

Online hbiss

  • Administrator
  • Location: Westchester County, NY
  • Posts: 2863
Re: In Slab Conduit - Failed Inspection
« Reply #22 on: February 06, 2016, 11:03:52 AM »
Quote
The problem is that the NEC doesn't address the specific situation that Larry's company encountered.  It shouldn't have.  This is not a matter of life safety and property protection, which is the intent of the NEC.

Exactly. It's a design issue and if the cable deteriorates in a few years and has to be replaced it isn't hurting anybody except the customer's bank account.

The NEC has been overstepping its boundaries ever since they became controlled by manufacturers looking to sell their products. Maybe it's time for somebody else to create a competing code reference that is not influenced by outside interests. The NEC is only a text book after all and since it's the only game in town, states and municipalities have no choice but to use it to base their laws on.

-Hal
I gotta get out of this business...


COMSYSTEC- Phone Systems | paging systems | background music systems | foreground music systems | retail music | restaurant music

Offline tonyburkhart

  • Moderator
  • Location: Reynoldsburg Ohio USA
  • Posts: 993
    • www.burkhartinc.com
Re: In Slab Conduit - Failed Inspection
« Reply #23 on: February 09, 2016, 09:35:43 AM »
Great information from all, thanks guys! Love this board 
Thanks,
Tony Burkhart
Burkhart Inc.
www.burkhartinc.com

Offline NFCphoneman

  • Moderator
  • Location: Jacksonville & Gainesville, FL
  • Posts: 649
    • Jacksonville Telephone Systems
Re: In Slab Conduit - Failed Inspection
« Reply #24 on: February 11, 2016, 03:05:47 PM »
Just an FYI, I did find a cable that can be used (at least according to the manufacturer) in wet locations and is rated CM.  It won't be of much help in a plenum, or between floors.

http://www.mohawk-cable.com/images/news/product-announcements/VersaLAN%205e%20NPB.pdf

Of course it costs 2-3 times as much as CMP.

Online hbiss

  • Administrator
  • Location: Westchester County, NY
  • Posts: 2863
Re: In Slab Conduit - Failed Inspection
« Reply #25 on: February 11, 2016, 04:13:12 PM »
Nice. It looks like you did some digging and it's good to know that this cable exists.

Quote
VersaLAN Indoor/Outdoor is listed by Underwriters Laboratories as National Electrical Code article 800 type CM rated communications cables. It meets Category 5e specifications of TIA/EIA-568-B.2 to support the operation of 1GBase-T over 100 meters. Transmission will employ full-duplex (transmitting and receiving simultaneously) over all four-pairs. The cable meets NEC article 800 Type CM.2005 NEC 800 communications cable listing requirements to be used in a building (NEC 800.113).

I see that they agree with me that data cabling is Art 800. :054:

-Hal
I gotta get out of this business...


COMSYSTEC- Phone Systems | paging systems | background music systems | foreground music systems | retail music | restaurant music

Offline tonyburkhart

  • Moderator
  • Location: Reynoldsburg Ohio USA
  • Posts: 993
    • www.burkhartinc.com
Re: In Slab Conduit - Failed Inspection
« Reply #26 on: February 14, 2016, 09:22:03 PM »
Just an FYI, I did find a cable that can be used (at least according to the manufacturer) in wet locations and is rated CM.  It won't be of much help in a plenum, or between floors.

http://www.mohawk-cable.com/images/news/product-announcements/VersaLAN%205e%20NPB.pdf

Of course it costs 2-3 times as much as CMP.


Awesome! I'll see how much we pay, and update. 2-3 x CMP is huge!
Thanks,
Tony Burkhart
Burkhart Inc.
www.burkhartinc.com

Offline tonyburkhart

  • Moderator
  • Location: Reynoldsburg Ohio USA
  • Posts: 993
    • www.burkhartinc.com
Re: In Slab Conduit - Failed Inspection
« Reply #27 on: February 15, 2016, 08:20:53 AM »
$335.45 per 1,000 foot box was our quote
Thanks,
Tony Burkhart
Burkhart Inc.
www.burkhartinc.com

Offline Rcaman

  • Member
  • Location: Pittsburgh, PA
  • Posts: 6
    • Americom, Inc.
Re: In Slab Conduit - Failed Inspection
« Reply #28 on: September 10, 2016, 04:10:42 PM »
Belden 7929A. This cable is MSHA rated and meets the NEC requirements.

Rcaman